    New MM350P Electrical rant

    I ordered a new 350P last Wednesday (supposed to be here Monday) and I wanted to go ahead and get the electrical done. I went to the Miller site and downloaded the manual and here is what it says.

    Input voltage 230V
    Input Amperes At Rated output 61
    Max Recommended Standard Fuse 90
    Min Input Conductor Size in AWG 8
    Min Grounding Conductor Size 8

    Now if I didn't know better, I might have used a 90 amp breaker with #8 wire. Why would Miller put something like this in the manual?
    I know that they are saying the you can use a "MAX" 90 amp breaker and a "MIN" #8 wire, but they don't tell you that if you use that #8 wire you need a 40 amp breaker or if you use the 90 amp breaker you need to use a larger wire (#2 maybe, I'd have to look that one up)

    I used #6 from the box to the outlet (about 35') and I'm gonna make up a 50 foot 6ga. So extension cord. I already have a 70 amp breaker and some of the charts that I have seen say the the 6ga will carry 70 amps. I will buy a 50 or 60 amp breaker if you think that is necessary.

  2. #2
    Join Date
    Jan 2004
    Location
    Browns Valley, CA
    Posts
    8,518
    Jmb,

    If you read NEC Art. 630, you'll find that what the Miller manual says is true. The numbers you quoted are per Art. 310 for 80% duty "standard" circuits. The welder's duty cycle allows the de-rated conductors per Art. 630.

    Just talked about that in the "What size breaker" thread.

    Hank
    ...from the Gadget Garage
    MM 210 w/3035, BWE
    HH 210 w/DP 3035
    TA185TSW
    Victor O/A "J" series, SuperRange
    Avatar courtesy of Bob Sigmon...

  3. #3
    Join Date
    Dec 2003
    Location
    Brownwood, Texas
    Posts
    186
    Quote Originally Posted by hankj
    Jmb,

    If you read NEC Art. 630, you'll find that what the Miller manual says is true. The numbers you quoted are per Art. 310 for 80% duty "standard" circuits. The welder's duty cycle allows the de-rated conductors per Art. 630.

    Just talked about that in the "What size breaker" thread.

    Hank
    Thanks Hank,
    It didn't dawn on me about the duty cycle derating...lol.
    But, like you stated in your post on "what size breaker" thread. If I installed the 90 amp breaker with #8 wire and moved, the next owner might be in for a surprise.
    Will I be okay with the #6 and the 70 amp breaker that I already have or should I buy a 60 amp breaker just to be safe.

  4. #4
    Join Date
    Jan 2004
    Location
    Browns Valley, CA
    Posts
    8,518
    #6 THHN and like inulated wire is good to 75 amps. (Art. 310, Table 310.16) You're good to go.

    Hank
    ...from the Gadget Garage
    MM 210 w/3035, BWE
    HH 210 w/DP 3035
    TA185TSW
    Victor O/A "J" series, SuperRange
    Avatar courtesy of Bob Sigmon...

  5. #5
    Join Date
    Mar 2003
    Location
    Brethren, Mi
    Posts
    11,282
    You can use 8 on circuits to 100A for some welding machines, but you have a good point not to leave it that way where someone may assume its a general use 100A circuit. The 6 wire and a 70A breaker (great if you already have one) is fine.

  6. #6
    Join Date
    Dec 2003
    Location
    Brownwood, Texas
    Posts
    186
    Thanks a bunch fellas!!!
    I should be burning wire by tommorrow afternoon if the machine comes in.