    What size Circuit Breaker?

    What size Circuitbreaker is reccomended for a 235 amp ac stick welder?
    Also what size wire for circuit?

    OLddog

  2. #2
    Join Date
    Mar 2003
    Location
    Brethren, Mi
    Posts
    11,282
    50 amp breaker.

  3. #3
    Join Date
    Mar 2004
    Location
    Cedar Rapids, IA
    Posts
    1,943
    A 50 amp normal breaker, 40 amp time delay and #10 wire is what is recommended for up to 250 amp welder.
    Jim-bee

  4. #4
    Join Date
    Oct 2004
    Location
    Brentwood Bay B.C.
    Posts
    104
    My welder says the primary amps are 45.5 would it be ok to run it of a 50 amp breaker?
    Last edited by J-Dogg; 01-15-2005 at 11:23 AM. Reason: can't type
    Keep On Truckin'

  5. #5
    Join Date
    Mar 2003
    Location
    Brethren, Mi
    Posts
    11,282
    Yes, these machines are designed to run from 50A circuits. Also we have been recommending 6 wire due to a number of factors that are listed in another thread. If it is only for a welder a number 8 is fine too as long as other types of equipment will not be used on this circuit.