What size Circuitbreaker is reccomended for a 235 amp ac stick welder?
Also what size wire for circuit?
OLddog![]()
Where to Buy
Service & Support
e-Learning
Weld Talk
What size Circuitbreaker is reccomended for a 235 amp ac stick welder?
Also what size wire for circuit?
OLddog![]()
50 amp breaker.
A 50 amp normal breaker, 40 amp time delay and #10 wire is what is recommended for up to 250 amp welder.
Jim-bee
My welder says the primary amps are 45.5 would it be ok to run it of a 50 amp breaker?
Last edited by J-Dogg; 01-15-2005 at 11:23 AM. Reason: can't type
Keep On Truckin'
Yes, these machines are designed to run from 50A circuits. Also we have been recommending 6 wire due to a number of factors that are listed in another thread. If it is only for a welder a number 8 is fine too as long as other types of equipment will not be used on this circuit.
Last edited by Sberry; 01-15-2005 at 11:53 AM.